Continuation from another thread that I was hijacking... /Sorry @danb35
So when I moved my "Server Room" to the basement closet; it ended up directly below that upward leg of the run in the basement. I simply tapped into that and installed my main rack outlets in the closet. Using 12 gauge wiring.
I do agree that if it was a longer run 8 gauge would be better, but from the panel to the Server closet is ~ < 30' so 10 gauge should be fine.
Actual plug on the UPS is not molded; but the type that can be disassemble by removing the screws. While the UPS does "cold boot" fine, I will check to see if there is any issues with the wiring to the plug (with the batteries removed...). Heck, should grab my multi-meter and at least do a continuity test..
As it stands now, I know that trying to use the existing outlet (2 pole / 20 amp breaker with 12 gauge wiring) is not recommended and have stopped pursuing that (was just curios to get the unit to fire up like Danb35 did). I will wait until I get that 30 amp breaker in and dedicated outlet in place. In the end, I figure that even if it turns out that the UPS is faulty I still want that dedicated outlet in there for when I get/have a working ups.
Will be extra careful for sure, while I am comfortable with wiring; high voltage/amp electrical stuff is one of those things that scares the heck out of me. While I don't get too concerned when messing with a normal 120v/15amp outlet; mucking around in a panel is not something to be taken lightly at all. I will get the wiring ran and outlet set first then tap into the panel last. But will for sure cut off all electricity to the panel first when I am doing that part.
Update: Panel is actually out of slots for breakers... So should I consider swapping out that existing 2 pole 20 amp breaker and having it replaced with a 2 pole 30 amp? Will get the wiring replaced with 10 (if not 8 gauge) as well. Only thing that concerns me is that original breaker was put in as a dedicated one for the server rack and I don't want to jeopardize anything in there. Of course most (if not all) will be plugged into the UPS, but it is nice to have a standard outlet for non-critical stuff.
Yeah, original breaker and wiring was install by an electrician. I had it ran from my basement panel across the length of the house and then up to the garage. That is where I originally had the Server Rack stored. Electrician used a dedicated single two pole breaker and I had him install one of those "whole house" surge protectors. All this was done using 12 gauge wiring.please call a licensed electrician, I wouldn't want your house to burn!
So when I moved my "Server Room" to the basement closet; it ended up directly below that upward leg of the run in the basement. I simply tapped into that and installed my main rack outlets in the closet. Using 12 gauge wiring.
I do agree that if it was a longer run 8 gauge would be better, but from the panel to the Server closet is ~ < 30' so 10 gauge should be fine.
Actual plug on the UPS is not molded; but the type that can be disassemble by removing the screws. While the UPS does "cold boot" fine, I will check to see if there is any issues with the wiring to the plug (with the batteries removed...). Heck, should grab my multi-meter and at least do a continuity test..
As it stands now, I know that trying to use the existing outlet (2 pole / 20 amp breaker with 12 gauge wiring) is not recommended and have stopped pursuing that (was just curios to get the unit to fire up like Danb35 did). I will wait until I get that 30 amp breaker in and dedicated outlet in place. In the end, I figure that even if it turns out that the UPS is faulty I still want that dedicated outlet in there for when I get/have a working ups.
Will be extra careful for sure, while I am comfortable with wiring; high voltage/amp electrical stuff is one of those things that scares the heck out of me. While I don't get too concerned when messing with a normal 120v/15amp outlet; mucking around in a panel is not something to be taken lightly at all. I will get the wiring ran and outlet set first then tap into the panel last. But will for sure cut off all electricity to the panel first when I am doing that part.
Update: Panel is actually out of slots for breakers... So should I consider swapping out that existing 2 pole 20 amp breaker and having it replaced with a 2 pole 30 amp? Will get the wiring replaced with 10 (if not 8 gauge) as well. Only thing that concerns me is that original breaker was put in as a dedicated one for the server rack and I don't want to jeopardize anything in there. Of course most (if not all) will be plugged into the UPS, but it is nice to have a standard outlet for non-critical stuff.